Preferred Stop Command
Is there a preferred stop command when using the advanced motor control commands? For instance, I use a lot of commands 65, 66, and 67 for motions that are long on a human scale, and sometimes I'd like to stop the motors before the motion finishes. It seems that there are a few different choices to stop, but are the behaviors any different? What command does the IonMotion big stop button use? Thanks.
- Basicmicro Support
- Posts: 1594
- Joined: Thu Feb 26, 2015 9:45 pm
Re: Preferred Stop Command
The IonMotion stop button sends a 0 Duty command. For an E-Stop situation you should use the Duty commands to stop. Since they take no feedback, once they are sent the motor is going to stop.
For velocity commands use a 0 speed velocity command, with or without accel to produce a controlled stop(eg not an e-stop).
For position commands, if you know where you want the new stop to be, send a new position command with that position, otherwise use the 0 Duty(with or without accel), or if you are using a cascaded velocity/position pid, use a 0 speed velocity command.
For velocity commands use a 0 speed velocity command, with or without accel to produce a controlled stop(eg not an e-stop).
For position commands, if you know where you want the new stop to be, send a new position command with that position, otherwise use the 0 Duty(with or without accel), or if you are using a cascaded velocity/position pid, use a 0 speed velocity command.
Re: Preferred Stop Command
Thanks for the clarification, this is exactly what I was looking for.